I refer to Kalgoorlie’s power generation. (1) What is the installed capacity of Western Power’s diesel turbines in Kalgoorlie? (2) What is the capacity of the line that connects to the main power grid? (3) To what capacity were they commissioned during the last power outage, which occurred on Wednesday, 18 February 2004? Hon TOM STEPHENS
AnswerView source ↗
The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(1) What is the installed capacity of Western Power’s diesel turbines in Kalgoorlie? (2) What is the capacity of the line that connects to the main power grid? (3) To what capacity were they commissioned during the last power outage, which occurred on Wednesday, 18 February 2004? Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(2) What is the capacity of the line that connects to the main power grid? (3) To what capacity were they commissioned during the last power outage, which occurred on Wednesday, 18 February 2004? Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(3) To what capacity were they commissioned during the last power outage, which occurred on Wednesday, 18 February 2004? Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(1) What is the installed capacity of Western Power’s diesel turbines in Kalgoorlie? (2) What is the capacity of the line that connects to the main power grid? (3) To what capacity were they commissioned during the last power outage, which occurred on Wednesday, 18 February 2004? Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(2) What is the capacity of the line that connects to the main power grid? (3) To what capacity were they commissioned during the last power outage, which occurred on Wednesday, 18 February 2004? Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(3) To what capacity were they commissioned during the last power outage, which occurred on Wednesday, 18 February 2004? Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
Hon TOM STEPHENS replied: The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
The Minister for Energy provides the following reply. Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
Western Power has advised the minister that - (1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(1) Western Power has two diesel-fired generating turbines of 35 and 20-megawatt capacity, totalling 55 megawatts. (2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(2) These two units are directly connected to the 220-kilovolt system via their own transformers, with no capacity restrictions. The 220-kilovolt line capacity is a complex issue that depends on the amount of generating plant active in the Kalgoorlie area. An indicative figure would be about 100 megawatts being transferred from Kalgoorlie to Perth. (3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
(3) Both units were used on the Monday and Tuesday; however, the smaller unit was unavailable on Wednesday. This did not impact on available power supplies as the emergency restrictions reduced the system demand to a level within Western Power’s generating capacity.
Explore WA Government Data
Search the full archive in the free dashboard, or query programmatically via API.
Explore more
Government Gazette
Appointments, regulatory notices, planning changes.
Hansard
Debates, questions, speeches and sentiment.
Tabled Papers
Reports and documents tabled in Parliament.
Committees
Committee profiles and recent reports.
Regulations
Subsidiary legislation with filters and summaries.
Bills
Proposed laws and parliamentary progress.
Acts
Current WA legislation and summaries.
Explanatory Memoranda
Bills with EMs (text/PDF) available.
Members
MP profiles, party breakdown and rankings.
Pollie Rankings
Data-driven rankings across 19 categories.
Amendment Chains
Track how schemes and regulations evolve over time.