A WA parliamentary question on notice addresses power outages in the southeast corridor, inquiring about frequency, duration, causes, the Ranford Road feeder's operational status, and other mitigation initiatives. The Minister for Energy provides a detailed response including outage statistics, causes, and planned improvements.

AnsweredQoN 4705Legislative Council
Asked
3 April 2007
Portfolio
Energy

QuestionView source ↗

(1) How many power outages have occurred in the southeast corridor since 1 December 2006?
(2) What is the duration of each power outage?
(3) What was the cause of each power outage?
(4) Given that the Ranford Road feeder is supposed to have the greatest impact on reducing power outages in the southeast corridor, and that its proposed operational date of mid March has passed, when will the feeder become operational?
(5) What other initiatives are being implemented to minimise outages in the southeast corridor?

AnswerView source ↗

Answered
29 May 2007
Responded by
Leader of the House representing the Minister for Energy
Response time
56 days
The Minister for Energy has provided the following response: (1) Western Power has taken the southeast corridor to mean the areas supplied from the Gosnells and Southern River zone substations. This comprises 13 suburbs supplied either in part or all by the Gosnells Substation. These suburbs include Beckenham, Canning Vale, Gosnells, Huntingdale, Kelmscott, Kenwick, Langford, Maddington, Martin, Orange Grove, Southern River, Thornlie and Westfield. Since December 2006, 151 power outages have occurred somewhere on these lines. It is important to note that the number of customers affected by an outage can vary from two customers to several thousand customers. (2) Outages ranged in duration from a few minutes to many hours. The average duration of outages in the southeast corridor for the period specified was 123 minutes. Pole top fires, which often require a pole or crossarm to be replaced, and therefore result in a lengthy outage had a significant impact on the average duration. (3) Causes of the outages included: Birds. Equipment failure. Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
(1) Western Power has taken the southeast corridor to mean the areas supplied from the Gosnells and Southern River zone substations. This comprises 13 suburbs supplied either in part or all by the Gosnells Substation. These suburbs include Beckenham, Canning Vale, Gosnells, Huntingdale, Kelmscott, Kenwick, Langford, Maddington, Martin, Orange Grove, Southern River, Thornlie and Westfield. Since December 2006, 151 power outages have occurred somewhere on these lines. It is important to note that the number of customers affected by an outage can vary from two customers to several thousand customers. (2) Outages ranged in duration from a few minutes to many hours. The average duration of outages in the southeast corridor for the period specified was 123 minutes. Pole top fires, which often require a pole or crossarm to be replaced, and therefore result in a lengthy outage had a significant impact on the average duration. (3) Causes of the outages included: Birds. Equipment failure. Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Since December 2006, 151 power outages have occurred somewhere on these lines. It is important to note that the number of customers affected by an outage can vary from two customers to several thousand customers. (2) Outages ranged in duration from a few minutes to many hours. The average duration of outages in the southeast corridor for the period specified was 123 minutes. Pole top fires, which often require a pole or crossarm to be replaced, and therefore result in a lengthy outage had a significant impact on the average duration. (3) Causes of the outages included: Birds. Equipment failure. Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
(2) Outages ranged in duration from a few minutes to many hours. The average duration of outages in the southeast corridor for the period specified was 123 minutes. Pole top fires, which often require a pole or crossarm to be replaced, and therefore result in a lengthy outage had a significant impact on the average duration. (3) Causes of the outages included: Birds. Equipment failure. Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
(3) Causes of the outages included: Birds. Equipment failure. Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Birds. Equipment failure. Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Equipment failure. Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Fire, other than pole top fires. Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Planned outages while upgrade work is carried out. Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Pole top fires. Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Transmission failure. Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Unknown. Interference with the power line has occurred and a subsequent patrol of the line has failed to find conclusive evidence. The interference is not generally related to equipment failure and can be caused by tree branches or other kinds of interference. Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Vehicles. Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Wilful damage. Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
Wind including wind borne debris. (4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
(4) The Ranford Road feeder became fully operational19 April 2007. (5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
(5) There are a number of maintenance and operational initiatives that are planned: · Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
· Minor reconfiguration of part of the network supplied by the Gosnells substation. The reinforcement work is now complete except for the commissioning of four reclosers. The reclosers are installed and ready to be commissioned in the very near future. · Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
· Targeted maintenance and inspection for some of the Gosnells feeders; · Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
· Targeted replacement of conductors and other equipment on parts of the network; · Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
· Pole siliconing to reduce the likelihood of pole top fires; · Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.
· Installation of automated switching devices on the network to improve outage restoration and minimise customer impact in the event of an outage.